Central DHW Controls in the 2010/12 Multifamily Energy Efficiency Rebate Program. ACEEE s Hot Water Forum May 13, 2010
|
|
- Mae Carpenter
- 5 years ago
- Views:
Transcription
1 Central DHW Controls in the 2010/12 Multifamily Energy Efficiency Rebate Program ACEEE s Hot Water Forum May 13,
2 Background Controls incentivized in statewide MF Energy Efficiency Rebate (MFEER) Expected savings of 34 and 45 therms/yr-apt for post-1970 and pre-1970, respectively Measured savings averaged 14, 12, and ¼ therms/yr-apt across three control manufacturers (25% realization rate) PG&E pulled the plug and Sempra searched for a new approach 2
3 Findings and Recommendations Based on: Study of 139 systems with temp modulation controls; including billing analysis Surveys of installers and controls manufacturers Meetings with installers and manufacturers following the report 3
4 Sempra Did Not Want to Pull the Plug In CA, there are 4.2 Million MF households About ½ in SoCalGas and SDG&E s territory The 4.2M pay about $.7 Billion per year for DHW In much of Sempra s area, energy/household for DHW is greater than energy for heating and cooling combined. 4
5 Typical MF Details Average Usage: 208 therms/apt ( range) 9200 therms/pump ( ,900 range) 236 gal storage ( range) 44 units per loop ( range) Built in 1940 ( range) 29,000 sq.ft. (9700 to 55,000) 5
6 SoCalGas MFEER Program: Changes for 2010/12 SoCalGas Central DHW Quality Control Manual Training for installers and inspectors Checklists for installers and inspectors Safety requirements & minimum measures Improved inspections (100% pre-inst. Inspections) Site Operators Manuals and site-personnel education Considered but rejected pay-for-performance 6
7 Customer Info System Info Installer s Pre- Installation Checklist Site (or Site_Nbr) Customer of Record Address City, zip Co. Contact Person Title Contact Phone/ Site Contact Person Title Contact Phone/ Contractor Info Supply (HWS) Pipe Size Insulation Return (HWR) Pipe Size Insulation Pump Size Pump Manufacturer Existing Control Condition (e.g., leaks, overly hot) Isolation Valves? Bleeder Valve? Backflow valve at CWS? Anti-scald mixing valve? Boiler/Water Heater Example Contractor Name Information Phone Location In Bldg Roof Contact Name Pressure Regulator 85# Installer Name General Description Forced General Property Info of the Boiler System Draft Not on a Qualifying System Boiler Manufacturer Ray Pak No. Apts Boiler Model # WH A No. Buildings Boiler Serial # abc Laundry facilities Built-in Storage 0 Washers Other Storage one 200 gal tank Dryers No. Burners or two Swimming Pool BTU In 600,000 Spa(s) BTU Out 492,000 rated Hydronic Heat Boiler HP unk. Barbecues Age of burner aprox. 15 yr Other Gas Meters (list acct. no. below, indicating system(s) associated with each meter) Temp of H 2 O in Setting or Reading Account No. Temp of H 2 O out 132 Describe Meter Configuration: Setting or Reading 130 If the system includes an Anti-Scald Mixing Valve, provide a sketch of how it fits in the system, note the building HWS setpoint temperature, and describe how your control will interact with the ASM valve to produce energy savings. Primary Loop Location and Operation Primary Loop 165 watts P.L. return line; l 1.25" 7 Comments/Other:
8 Inspector s Post-Installation Checklist Date: System Info Customer/Acct. Info SoCalGas Acct. No. NOTE: "Secondary Loop" is between the HW storage Seconday Loop Pump & Piping tank and the end users. Control: Manufacturer "Primary Loop" is between Site (or Site_Number) Model Number or Name the boiler and storage tank. Customer of Record Site Address Supply (HWS) Pipe Insulation City, zip Return (HWR) Pipe Insulation Company Contact Person Pump: Pump Manufacturer Title Wattage Contact Phone/ Leaks? Overly hot? Unsusual noise? Contractor Name Isolation Valves? Contact Phone/ Bleeder Valve? Boiler/Water Heater Gas Meter Identification Information Example Meter No. (1) Location In Bldg Roof Meter No. (2) Boiler Manufacturer Ray Pak Meter No. (3) Boiler Model # WH A Meter No. (4) Boiler Serial # abc def Site Contact Person Insp.? Temp of H 2 O in 78 Name Setting or Reading 125 Title Temp of H 2 O out 132 Contact Phone/ Setting or Reading 130 Final Inspection Unsafe Conditions Left? Site Cleaned Up? Operator's Guide Site? Site Prsnl. Instructed by Installer? System Operating Correctly? Yes No Notes Comments/Other: Inspector's Name Inspector's Signature 8
9 Questions? Nehemiah Stone Principal Benningfield Group Inc. (916)
DHW Measures and Concepts
DHW Measures and Concepts Multi-Family Energy Measures Webinar Series January 12, 2011 Sponsored by PG&E PG&E refers to Pacific Gas and Electric Company, a subsidiary of PG&E Corporation. 2010 Pacific
More informationWATER HEATING PAGETTE
WATER HEATING PAGETTE HISTORY PAGette Started July 2005 Based on PAG meeting comments PAG members suggested we form group to examine Water Heating opportunities PAGette to report back to the PAG on its
More informationEMERGING TECHNOLOGIES PROGRAM. Overview - ACEEE Hot Water Forum Session 7D
EMERGING TECHNOLOGIES PROGRAM Overview - ACEEE Hot Water Forum Session 7D February 24, 2015 1 4 Case Studies 1. MFR Shared Combo HW Boiler Reset Controller Comparison Field Testing 2. Residential Recirc
More informationWater and Space Heating Nonresidential HVAC Stakeholder Meeting #2
1 Water and Space Heating Nonresidential HVAC Stakeholder Meeting #2 California Statewide Utility Codes and Standards Program Heschong Mahone Group, Inc. Portland Energy Conservation, Inc. CTG Energetics
More informationCASE STUDY: HIGH EFFICIENCY HOT WATER SYSTEMS IN A COMMERCIAL KITCHEN. For the 2019 ACEEE Hot Water Forum, Nashville, TN
CASE STUDY: HIGH EFFICIENCY HOT WATER SYSTEMS IN A COMMERCIAL KITCHEN For the 2019 ACEEE Hot Water Forum, Nashville, TN March 12, 2019 Stephen Walmsley 1 4 Purpose and Goals» Understand the importance
More informationGaining Efficiencies Through Hot Water
Gaining Efficiencies Through Hot Water Carlos Ruiz, Residential Programs Supervisor ACEEE Water Heater Forum Ontario, CA May 13, 2010 This information is provided solely for informational purposes. Although
More informationControl Panel Checklist
Control Panel Checklist Versatronik -C Panel Checklist Option Selection for Control Panel Quotes Checklist Control Panel Checklist Section 1 General Information Customer name Phone number Fax number Email
More informationHot Water Heating and Distribution Possible CASE Initiatives for 2011 T24 Standards
Hot Water Heating and Distribution Possible CASE Initiatives for 2011 T24 Standards ACEEE Hot Water Forum Ontario, CA 5/13/2010 Bradley Meister, P.E. Energy Efficiency Research Office Energy Research and
More informationReaching New Heights in Efficient Water Heating Technologies
Reaching New Heights in Efficient Water Heating Technologies Carlos Ruiz, Residential Programs Supervisor ACEEE Water Heater Forum Montrerey, CA June 8, 2009 This information is provided solely for informational
More informationThis presentation is posted for public use. ACEEE does not endorse any product or service.
This presentation is posted for public use. ACEEE does not endorse any product or service. ACEEE accepts no responsibility for any facts or claims this presentation may contain. CO 2 Heat Pump Water Heater
More informationAM SERIES BOILER INSTALLATION FORM
AM SERIES BOILER INSTALLATION FORM Please complete one (1) form for each SITE containing AM Series BOILERS. Return to AERCO for warranty validation within 30 days of start-up. After completion, e-mail
More informationPerformance of Solar Water Heating Systems in the United States
Performance of Solar Water Heating Systems in the United States Danny Parker & Camilo Gil Florida Solar Energy Center ACEEE Hot Water Forum June 2009, Asilomar,, California Rebate situation in Florida
More informationMultifamily Buildings: Real World Monitored Data on Hot Water Energy and Water Use
Multifamily Buildings: Real World Monitored Data on Hot Water Energy and Water Use BuildingEnergy Boston Conference March 8, 2017 Presented by: Andrew Proulx, P.E., LEED AP Neil Donnelly, E.I.T. New Ecology,
More informationMODULEX BOILER INSTALLATION FORM
MODULEX BOILER INSTALLATION FORM Please complete ONE (1) form for each SITE and return to AERCO for warranty validation within 30 days of start-up. After completion, e-mail this form to: STARTUP@AERCO.COM.
More informationApplication and Terms and Conditions
Multi-Family Prescriptive Program Instructions for Use Prescriptive projects with rebates greater than 3,000 must receive pre-approval from the program BEFORE project installation begins. For detailed
More informationVersa- Hydro. up to 96% Efficient
Versa- Advanced Heating & Hot Water Systems Hydro up to 96% Efficient The cost effective Versa-Hydro combines space heating, domestic hot water, and total system control into one compact, high efficiency
More informationTHE CITY OF NORTH RIDGEVILLE 7307 AVON BELDEN ROAD, NORTH RIDGEVILLE, OHIO TELEPHONE: (440) FAX: (440) Building Department
7307 AVON BELDEN ROAD, NORTH RIDGEVILLE, OHIO 44039 TELEPHONE: (440) 353-0822 FAX: (440) 353-0823 INSTRUCTIONS FOR SWIMMING POOLS REQUIREMENTS FOR PERMIT: Completed application form Plot plan showing lot
More information"Best Practices in Modern Hydronic Heating - THE DETAILS
"Best Practices in Modern Hydronic Heating - THE DETAILS 190 supply water temperature (ºF) 170 150 130 110 90 fin-tube convector (RR=1.38) panel radiator (RR=1.0) thin slab rad. floor (RR=0.69) slab r
More information2009 CALIFORNIA RESIDENTIAL APPLIANCE SATURATION STUDY
CONSULTANT REPORT 2009 CALIFORNIA RESIDENTIAL APPLIANCE SATURATION STUDY Volume 2: Results Prepared for: Prepared by: California Energy Commission KEMA, Inc. OCTOBER 2010 CEC 200 2010 004 Prepared by:
More informationClearFire - Hydronic Startup Report
ClearFire - Hydronic Startup Report Date Serial No. THIS FORM IS FOR MODEL CFC / CFW CLEARFIRE BOILERS Customer s Name Location Model Design Pressure Working Pressure Rated Input (nameplate rating) BTU/hr
More informationCONTROLLED CHILLED BEAM PUMP MODULE
FIRST COST SAVINGS PROACTIVE CONTROL CONTROLLED CHILLED BEAM PUMP MODULE Active condensation control system effectively eliminates chilled beam condensation High efficiency, variable speed pump uses a
More informationProcess Air Compressors, Boilers, and Water Heaters Stakeholder Meeting 2
Process Air Compressors, Boilers, and Water Heaters Stakeholder Meeting 2 California Statewide Utility Codes and Standards Program Energy Solutions Heschong Mahone Group, Inc. Portland Energy Conservation,
More informationInstallation & Operation Manual Models: TSU
TSU-I-O Rev A Installation & Operation Manual Models: TSU 150-940 CAUTION: This appliance is not intended for potable water. This manual must only be used by a qualified heating installer / service technician.
More informationTHE CITY OF NORTH RIDGEVILLE 7307 AVON BELDEN ROAD, NORTH RIDGEVILLE, OHIO TELEPHONE: (440) FAX: (440) Building Department
THE CITY OF NORTH RIDGEVILLE 7307 AVON BELDEN ROAD, NORTH RIDGEVILLE, OHIO 44039 TELEPHONE: (440) 353-0822 FAX: (440) 353-0823 Building Department INSTRUCTIONS FOR DECKS REQUIREMENTS FOR PERMIT: Completed
More informationStatewide Residential and Commercial Upstream High Efficiency Gas Water Heater Program. Robert Mowris Associates
Statewide Residential and Commercial Upstream High Efficiency Gas Water Heater Program Robert Mowris Associates 1-800-786-4130 Why is Water Heating Important? Residential and commercial gas water heating
More information2018 Rebate Catalog and Application
2018 Rebate Catalog and Application Save money on qualified Home Cooling Systems, Appliances and more. Read about rebates for your home and business at mid.org/rebates REV 01.2018 Modesto Irrigation District
More informationWilo Stratos Z vs. standard three piece bronze domestic recirc pump
Case Studies Wilo Stratos Z vs. standard three piece bronze domestic recirc pump This is a preliminary analysis of Wilo Z Domestic hot water recirculating pumps per our discussion last Tuesday. Following
More informationBuilding Department Informational Handout
City of Sonoma Building Department Informational Handout Residential Water Heaters Handout No: 15 Revised: 4/26/18 A water heater is an appliance designed to supply hot water and is equipped with automatic
More informationCONTROLLED CHILLED BEAM PUMP MODULE
ENERGY SAVINGS 1 ST COST SAVINGS PROACTIVE CONTROL CONTROLLED CHILLED BEAM PUMP MODULE Active condensation control system effectively eliminates chilled beam condensation High efficiency, variable speed
More informationHeat Pump Water Heaters: A Key Energy Technology for California
Heat Pump Water Heaters: A Key Energy Technology for California Passive House California April 2018 Danny S. Parker A Research Institute of the University of Central Florida Heat Pump Water Heaters (HPWH):
More informationBoilers and Water Heating Rebate Catalog Saving energy for a brighter future.
Pacific Gas and Electric Company Energy Efficiency s for Your Business Boilers and Water Heating Catalog Saving energy for a brighter future. Boilers and Water Heating Catalog Energy Efficiency s for Your
More informationAdvanced Heating & Hot Water Systems. High Efficiency Residential & Commercial Space Heating
Advanced Heating & Hot Water Systems High Residential & Commercial Space Heating SCAQMD Rule 1146.2 Combined DHW & Space Heating APPLICATION Mod Con Double Stack Mod Con Elite Elite FT MC Series Pioneer
More informationResidential Water Heating
Residential Water Heating Energy Design Conference, Duluth Ben Schoenbauer, CEE February, 25 th, 2014 In accordance with the Department of Labor and Industry s statute 326.0981, Subd. 11, This educational
More informationRebate Catalog. Save money on qualified Home Cooling Systems, Appliances and more. Read about rebates for your home and business at mid.
Rebate Catalog Save money on qualified Home Cooling Systems, Appliances and more. Read about rebates for your home and business at mid.org/rebates REV 12.31.2018 How to apply Modesto Irrigation District
More informationInstantaneous Water Heaters
2016 Title 24 Codes & Standards Enhancement (CASE) Proposal Instantaneous Water Heaters May 20, 2014 Sarah Schneider SSchneider@energy-solution.com 510-482-4420 ext. 202 Bijit Kundu Bkundu@energy-solution.com
More informationMul$family Buildings: Real World Monitored Data on Hot Water Energy and Water Use
Mul$family Buildings: Real World Monitored Data on Hot Water Energy and Water Use 2015 ACEEE Hot Water Forum February 24, 2015 Presented by: Andrew Proulx, P.E., LEED AP Neil Donnelly, E.I.T. New Ecology,
More informationJefferson Cocke County Utility District Marketing Plan (July 1, 2008 through June 30, 2019) Revised effective July 01, 2016 A) Identify commercial
` Jefferson Cocke County Utility District Marketing Plan (July 1, 2008 through June 30, 2019) Revised effective July 01, 2016 A) Identify commercial and home development before construction has begun (or
More informationPrescriptive Program Rebate Application
Application Prescriptive Program Application Check the appropriate program box for your rebate. Cooling FSO (Fluid System Optimization) Foodservice equipment Heating Lighting Motors & drives Customer information
More informationHVAC System Consideration$ 05/14/2012 SAVING MONEY IN HVAC SYSTEMS
SAVING MONEY IN HVAC SYSTEMS Rod Rhoads, GDS Associates Inc HVAC System Consideration$ What percent of a commercial business s energy usage comes from their HVAC system? How much money do commercial facilities
More informationInstantaneous Water Heaters (IWH)
FILE NO.: 115.20 DATE: Mar. 28, 2002 SUPERSEDES: New DATE: New Instantaneous Water Heaters Instantaneous Water Heaters (IWH) IWH Application Case Study Handbook Introduction This handbook provides the
More informationHow to Heat Water in All-Electric Homes & Apartments?
How to Heat Water in All-Electric Homes & Apartments? March 2015 NEW YORK, NY WASHINGTON, DC NORWALK, CT Robb Aldrich Steven Winter Associates, Inc. raldrich@swinter.com 1 AIA CEU Info Credit(s) earned
More informationBUILDING DEPARTMENT FEE SCHEDULE
BONDS HOUSE MOVING Site to site $ 5,000 Finishing $ 1,0 NOTE: Upon request, bonds may be obtained thirty () days after final inspection approval BUILDING PERMITS Building / Sign / Wrecking Permits Base
More information2018 Rebate Catalog and Application
2018 Rebate Catalog and Application Save money on qualified Home Cooling Systems, Appliances and more. Read about rebates for your home and business at mid.org/rebates REV 01.2018 Modesto Irrigation District
More informationDemand Side Management (DSM) Natural Gas
Demand Side Management (DSM) Natural Gas Summary: This initiative analyzes the potential of a natural gas efficiency standard (NGES) to promote the costeffective replacement of older, less efficient household
More informationWe can replace your refrigerator if it is built before December, 2000, OR if it tests as energy inefficient.
CLEARCorps Detroit Refrigerator Replacement Program Application Dear Community Member: July 2017 In partnership with DTE Energy, CLEARCorps Detroit can replace your old inefficient refrigerator for free
More informationHERS Verified Single Dwelling Unit Hot Water System Distribution (Page 1 of 6)
CEC- (Revised 03/15) HERS Verified Single Dwelling Unit Hot System Distribution (Page 1 of 6) A. General Information 01 Dwelling Unit Name B. Design HERS Verified Dwelling Unit Systems Information This
More informationMascot. Gas-Fired Residential and Commercial Wall-Mounted Boiler. Easy Installation, 96% Efficiency, Fully Condensing
Mascot Gas-Fired Residential and Commercial Wall-Mounted Boiler Easy Installation, 96% Efficiency, Fully Condensing Mascot is a high-efficiency, wall-mounted boiler available in three BTU sizes 126, 167,
More informationVe r s a - Hyd ro. 96% Efficient. The cost effec t i ve. ersa-hydro
ersa-hydro Versa- Hydro 96% Efficient The cost effec t i ve Ve r s a - Hyd ro combines space heating, domestic hot water, and total system control into one compact, high efficiency mod-con unit. I n n
More informationNPE-A and NPE-S Condensing Tankless Water Heaters
The Leader in Condensing Technology NPE-A and NPE-S Condensing Tankless Water Heaters Navien makes it easy to go tankless in residential and commercial applications. New NaviLink Wi-Fi remote control system...now
More informationMultifamily Energy Efficiency Rebates Application Package
Application Package Cash rebates are available for the installation of qualified energy efficiency products in apartment dwelling units and in the common areas of apartment complexes, condominium complexes,
More informationPath to Energy Savings & Solar
02.10.10 Path to Energy Savings & Solar Existing Residential and Small Commercial 2 Goals of this Webinar Provide the tools and inform you of the steps you should take before and after installing solar
More informationInspection Phase Three. Mechanical, Electrical & Plumbing Section 503
Inspection Phase Three Mechanical, Electrical & Plumbing Section 503 COMCheck Mechanical Field Inspection Checklist Mechanical Mechanical, Electrical & Plumbing Equipment Efficiencies But a lot ore too
More informationTECHNICAL INSTRUCTIONS
TECHNICAL INSTRUCTIONS Hardware Procedure: AERCO Buffer Tank Installation and Maintenance Applies to: Any applicable water heater/boiler piping system arrangement. Description of Document: This provides
More informationCOMcheck Software Version Review Mechanical Compliance Certificate
COMcheck Software Version 4.0.7.2 Review Mechanical Compliance Certificate Section 1: Project Information Energy Code: 2014 Oregon Energy Efficiency Specialty Code Project Title: Benton County Health Project
More informationNPE-A and NPE-S Condensing Tankless Water Heaters
The Leader in Condensing Technology NPE-A and NPE-S Condensing Tankless Water Heaters Navien makes it easy to go tankless in residential and commercial applications. New NaviLink Wi-Fi remote control system...now
More informationSEALED THERMAL STORE
ISSUE 3 0717 INSTALLATION AND USER GUIDE ENERGYMANAGER SEALED THERMAL STORE ADVANCE APPLIANCES LTD PLEASE RETAIN AND ENSURE SERVICE RECORDS ARE KEPT UP TO DATE. SCHEMATIC DIAGRAM OF ENERYMANAGER THERMAL
More informationUser's Manual MODEL DPW-099 DPW-120. Rev1. Please use this product after reading this User's Manual for your safety.
Rev1 User's Manual MODEL DPW-099 DPW-120 1. Safety Warnings 2 2. Names of Components 8 3. Proper Operation - Before Operation 10 - Cautions when in use 11 - Cautions to Prevent Freezing during the Winter
More informationBosch. Gas Condensing Boiler. Applications Manual. 100, 151 Combi Boiler 57, 100, 131, 151 Heating Boiler
WARNING: Improper installation, setup, modification, operation or maintenance of the heating system can cause personal injury and property damage. Follow each appliances' instructions precisely. For assistance
More informationNo Other Adequate Source of Heat (NOASH) Application for
No Other Adequate Source of Heat (NOASH) Application for 2018-2020 Thank you for taking the time to complete this application. Please refer to the criteria for exemption from Burn Bans, Solid Fuel Burning
More informationPlease make sure your application includes the following:
June 17, 2015 Dear Community Member: In partnership with DTE Energy, CLEARCorps Detroit can replace your old inefficient refrigerator for free with a new, efficient model from Lowe s. We can only replace
More informationSolar Water Heating Basics for Homeowners
Solar Water Heating Basics for Homeowners 1 1 What is Solar Water Heating? Solar Assist or Solar Pre-heat Always keep the existing heater as backup to solar Great way to conserve energy, reduce your utility
More informationWO 21: 2012 California Lighting and Appliance Saturation Study (CLASS)
ENERGY WO 21: 2012 California Lighting and Appliance Saturation Study (CLASS) Public Webinar: Key Findings and Introduction to Webtool Claire Palmgren JUNE 16, 2014 1 DNV GL 2013 June 16, 2014 SAFER, SMARTER,
More information96% AFUE Efficiency CONDENSING RESIDENTIAL GAS BOILERS CONTROL WITH ADVANCED USER FEATURES MODELS FROM 80,000 TO 285,000 BTU/HR
CONDENSING RESIDENTIAL GAS BOILERS CONTROL WITH ADVANCED USER FEATURES MODELS FROM 80,000 TO 285,000 BTU/HR 5:1 FIRING RATE MODULATION LESS THAN 20 ppm NOx DIRECT VENT FLEXIBILITY TO 100 FEET 96% AFUE
More informationHPWH Market Barriers & Best Practices JOSH BUTZBAUGH ACEEE HOT WATER FORUM MARCH 22, 2018
HPWH Market Barriers & Best Practices JOSH BUTZBAUGH ACEEE HOT WATER FORUM MARCH 22, 2018 1 Background Water heating is the second largest energy use in U.S. residences National Perspective - Electric
More informationEnergy-Efficiency Options for Residential Water Heating
Energy-Efficiency Options for Residential Water Heating Dave Bohac, PE Director of Research Center for Energy and Environment Duluth Energy Design Conference February, 2015 In accordance with the Department
More informationEnergy Efficiency Business Rebates Natural Gas Catalog
Energy Efficiency Business Rebates Natural Gas Catalog Solution Product Code Storage Water Heater G-A1 Storage Water Heater Natural Gas Products Product Description Units $/Unit Page # $2.00 3 Space Heating
More informationOutdoor Reset Control Theory FULL versus PARTIAL reset
Outdoor Reset Control Theory FULL versus PARTIAL reset Conventional boilers must be protected against sustained operation at low temperatures. If not, they will be damaged by sustained flue gas condensation.
More informationMinnesota Multifamily Rental Characterization Study
Minnesota Multifamily Rental Characterization Study Jeannette LeZaks February 25, 2014 Duluth Energy Design Conference CONTINUING EDUCATION In accordance with the Department of Labor and Industry s statute
More informationApplication Information
1. Complete the National Fuel Application, review the terms and conditions and sign the application form on page 2. New construction is also now eligible for this program in 2018. 2. Include the following
More information2010 PROCard PowerGuide
2010 PROCard PowerGuide 05 09 12 20 Tankless is Green Space Heating Less expensive technology No minimum flow requirement Wastes energy and money (costing money to heat water even when you re not using
More informationTubular Skylights aka Solar tubes aka Tubular Daylighting Devices (TDDs) ENERGY STAR windowto-door. After
Tubular Skylights aka Solar tubes aka Tubular Daylighting Devices (TDDs) ENERGY STAR windowto-door retrofit: Before After ENERGY STAR Clothes Washers Save 40% in energy and water compared to standard
More informationSingle Dwelling Unit Hot Water System Distribution Project Name: Enforcement Agency: Permit Number:
(Page 1 of 6) A. General Information 01 Dwelling Unit Name B. Design Dwelling Unit Systems Information This table reports the water heating system features that were specified on the registered CF1R compliance
More informationUpdate Dedicated Heat Recovery Chiller Technology. Don Frye. Gulf South
3/5/2018 1 Update Dedicated Heat Recovery Chiller Technology Don Frye Gulf South Good design is an intentional act Begin with the end in mind Basic Bldg Tenants IAQ (low VOC & CO 2 ) Controlled Temp &
More informationHot Water Distribution System Losses in a Net-Zero Home
Hot Water Distribution System Losses in a Net-Zero Home March 22, 2018 ACEEE Hot Water Forum William Healy Tania Ullah National Institute of Standards and Technology Overview of Presentation Purpose: To
More informationASPE Seminar Water Heater Piping Strategies Presented by Joe Kalarickal, EIT Regional Sales Manager AERCO International
ASPE Seminar Water Heater Piping Strategies Presented by Joe Kalarickal, EIT Regional Sales Manager AERCO International Presentation Overview Water Heater Piping Strategies How to size a water heater?
More informationCity of Gainesville Inspection Permitting Fees Effective July 1, 2012
City of Gainesville Inspection Permitting Effective July 1, 2012 BUILDING PERMITS New Construction of Residential Homes 0-200 square feet $40.00 Plus additional cost per square foot over 200 $0.20 Home
More informationDraft. used, copied, and. responsibility for copyrights
CODES AND STANDARDS ENHANCEMENT INITIATIVE (CASE) Draft Measure Information Template Water and Space Heatin ng ACM Improvement 2013 Californiaa Building Energy Efficiency Standards California Utilities
More informationOzone Laundry Fundamentals. Special guest: DEL Clean Ozone Laundry Systems
Ozone Laundry Fundamentals Special guest: DEL Clean Ozone Laundry Systems Presented by Nina Newhouser and John Grillo 11.11.2014 Speakers energysmart overview Rebates for your ozone laundry systems Rebates
More informationCombining Space and Water Heating with Highly Efficient Results
Combining Space and Water Heating with Highly Efficient Results Ben Schoenbauer, Center for Energy and Environment Jake McAlpine, Sustainable Resource Center 23 rd Annual Energy Design Conference and Expro
More informationPG&E 2014 Title 24 Extension Products Products were extended through July 1, 2014
Midstream PG&E 2014 Title 24 Extension Products Products were extended through July 1, 2014 FAMILY CODE DESCRIPTION IMPACTED DISCONTINUATION LED Refrigerated Case Lights with Occupancy Sensors occupancy
More informationDo Improved Hot Water Systems Result In Efficient Consumer Behaviors Conference Feb 29 Mar 2 Scottsdale, Arizona
Do Improved Hot Water Systems Result In Efficient Consumer Behaviors Why Does This Presentation Matter? Gain an understanding of what residents desire from their hot water service. Why Does This Presentation
More informationNPE-A and NPE-S Condensing Tankless Water Heaters
NPE-A and NPE-S Condensing Tankless Water Heaters Navien makes it easy to go tankless in residential and commercial applications. New NaviLink Wi-Fi remote control system...now available as an add-on accessory.
More informationNPE-A and NPE-S Condensing Tankless Water Heaters
The Leader in Condensing Technology NPE-A and NPE-S Condensing Tankless Water Heaters Navien makes it easy to go tankless in residential and commercial applications. New NaviLink Wi-Fi remote control system...now
More informationTURF REPLACEMENT PROGRAM, Fall 2018 INTAKE FORM
TURF REPLACEMENT PROGRAM, Fall 2018 INTAKE FORM PURPOSE The City of Boulder s Turf Replacement Program provides participants with the information, tools and materials needed to incentivize water conservation.
More informationHydronic Product & Application Catalog
Hydronic Product & Application Catalog Brazed Plate Heat Exchangers MJanuary 2005 for: Radiant Floor Heating Domestic Water Heating Snow Melt Swimming Pools Steam Close Approach High Pressure Systems Multi-Purpose
More informationBackflow Prevention Cross Connection Control Department can be contact at (956) or (956)
Backflow Prevention Cross Connection Control Department can be contact at (956) 983-6519 or (956) 983-6347 Revised July 2013 BACKFLOW PREVENTION ASSEMBLY INSTALLATION STANDARDS All backflow prevention
More informationResidential Heating Boilers
Residential Heating Boilers BAXI BAXI Luna Duo-Tec GA+ QUALITY HYDRONIC HEATING EQUIPMENT The best in European design & manufacturing giving you warmth, efficiency and total peace of mind. Residential
More informationBUILDING DIVISION. Multi-family Rental Inspection Program SELF-CERTIFICATION APPLICATION
SC_Application.doc (rev. 04/24/2017) BUILDING DIVISION Multi-family Rental Inspection Program SELF-CERTIFICATION APPLICATION Please refer to the Self-Certification Application, Affidavit and Checklist
More informationEnergy Efficient Options for Residential Water Heating
Energy Efficient Options for Residential Water Heating Feb 2018 Ben Schoenbauer, Senior Research Engineer Center for Energy and Environment In accordance with the Department of Labor and Industry s statute
More informationCOMPLIANCE INSPECTION CHECKLIST. Date: 5/14/2011 Time In: 12:30PM Time Out: 1:00PM
1030459 75790 PERCHLOROETHYLENE DRY CLEANERS COMPLIANCE INSPECTION CHECKLIST INSPECTION TYPE: ANNUAL (INS1, INS2) COMPLAINT/DISCOVERY (CI) RE-INSPECTION (FUI) ARMS COMPLAINT NO: AIRS ID#: 103 0459 Date:
More informationByrd Barr Place PSE HELP Program:
Byrd Barr Place PSE HELP Program: 2017-2018 Is My Household s Average Monthly Income at or Below the Following Amounts? Eligibility is based on the average monthly income my household received for the
More informationEnd customer overview
16210568-1 2016-08-23 End customer overview Indoor module with heat pump control 1. Sign the installation checklist. 2. Serial no. behind touchscreen. 3. Bleed radiator system and products, approx. one
More informationGet Wise to ThermWise. An Insider s Guide to ThermWise Rebates
Get Wise to ThermWise An Insider s Guide to ThermWise Rebates Table of Contents 3 4 5 6 7 8 9 10 11 12 13 14 15 Introduction FAQ Clothes Washer Gas Storage Water Heater Gas Tankless Water Heater Gas Condensing
More informationSPARE PARTS EXPLODED VIEW GAS WALL BOILERS Model CLAS. R EN - Edition 01-01/02/2007
SPARE PARTS EXPLODED VIEW GAS WALL BOILERS Model CLAS R8215828-01EN - Edition 01-01/02/2007 3300187 CLAS 24 NG (EAA1)...... 3300189 CLAS 24 CF NG (EAA1)...... 3300188 CLAS 28 NG (EAA1)...... Reference
More informationHot Water a Hot Commodity Better Buildings by Design, February 2012 Burlington, VT
Hot Water a Hot Commodity Better Buildings by Design, February 2012 Burlington, VT Gary Klein Affiliated International Management, LLC 916 549 7080 gary@aim4sustainability.com Gary Klein, 2012 Efficiency
More informationCompleted Projects / Projets terminés
Completed Projects / Projets terminés New Standards New Editions Special Publications Gas Technician Training 2 Module 10, 3rd edition Piping and Tubing Systems for Industrial and Commercial Applications...
More informationPrescriptive Rebate Application
Instructions for Use Some prescriptive projects must receive pre-approval from the program BEFORE project installation begins or equipment is purchased, as indicated in Step 1 below. For detailed instructions,
More informationYour floor to ceiling guide
Your floor to ceiling guide Saving energy really doesn t require a lot of your energy. There are some easy things you can do to make a difference in your monthly energy usage and still be comfortable.
More informationM2 Series Startup Form
M Series Startup Form Job Name: Date: Address: Model Number: Serial Number: Tag: Startup Contractor: Address: Phone: Pre Startup Checklist Installing contractor should verify the following items.. Is there
More informationQualifies for up to $ 1500 Energy Tax Credit! CONDENSING RESIDENTIAL GAS BOILERS CONTROL WITH ALL NEW, ADVANCED USER FEATURES
CONDENSING RESIDENTIAL GAS BOILERS CONTROL WITH ALL NEW, ADVANCED USER FEATURES 5 FLOOR-STANDING AND 5 WALL-MOUNT MODELS FROM 50,000 TO 285,000 BTU/HR FIRING RATE MODULATION TO 5:1 LESS THAN 20 ppm NOx
More information