Threaded. Flanged. Model PSH. Primary Secondary Header A-451

Similar documents
Domestic. Pump Series CB and CBE Condensate Units SINGLE OR DUPLEX 1,000 THRU 140,000 SQ. FT. EDR-250 THRU 34,748 LB./HR.

Water Piping and Pumps

LS Condensate Removal Pump INSTRUCTION MANUAL REVISION A

A Primary Concern by John Siegenthaler, P.E. October 1, 2005

INSTRUCTION MANUAL HS-229G

The Ultimate in Distribution Efficiency. Air Eliminator Dirt Separator Low Loss Header Hydraulic Separator

INSTRUCTION MANUAL A REVISION A. Series e 3-4/e 3-6 Instant Hot Water Recirculating Systems

Hydraulic Separation Moving Beyond Priamry / Secondary Piping...

Domestic Pump Series VCMD TM Combination Vacuum & Boiler Feed Unit

HYDRONICS BY JOHN SIEGENTHALER

HYDRONIC SPECIALTIES TACO MPT Tank(s) 05/30/2012. A. Multi-Purpose Tank buffer tank, air separator, and hydraulic decoupler

ecocirc XL HIGH EFFICIENCY LARGE WET ROTOR PUMP FOR HEATING, COOLING AND POTABLE WATER SYSTEMS A-162C

TECHNICAL. Series 18. Pump Packages

INSTRUCTION MANUAL MM-601REVI. Series FS4-3 General Purpose Liquid Flow Switch

Hoffman Specialty Pump Products

Commercial, Residential & Institutional Pumps, Tanks, & Accessories

INSTRUCTION MANUAL MM-615E. Series FS1 High Sensitivity Liquid Flow Switch

Allcan TM Installation Manual

WHY THE REMOVAL OF NONCONDENSABLE GASES AND AIR IS CRITICAL IN A STEAM SYSTEM

In-Line Air Separators

CALEFFI. SEP4 combination hydraulic, air, dirt and magnetic separator series 01249/13.1 NA. Replaces 01249/13 NA. Function.

2018 PLUMBING AND HYDRONICS CATALOG

DIRTCAL - DIRTMAG dirt separator

Hoffman Specialty Watchman Series WC & WCS Condensate Units Replacement Parts PART LISTS DN0436C

PATENTED TECHNOLOGY THE CORE OF ANY PROFESSIONAL HYDRONIC INSTALLATION

Function. Pressure Vessel Inspector; CRN registered Sizes 2 4

INSTALLATION INSTRUCTIONS WARRANTY

PATENTED TECHNOLOGY THE CORE OF ANY PROFESSIONAL HYDRONIC INSTALLATION

DIRTMAG dirt separator with magnet, adjustable for vertical or horizontal pipe

INSTRUCTIONS REHAU PRO-BALANCE MIXING MODULE

DISTRIBUTION SYSTEMS. Water Piping and Pumps

DESCRIPTION AND INSTALLATION

TOTAL SYSTEM EFFICIENCY: AN INTRODUCTION TO CONDENSING BOILERS. David Grassl PE Mechanical Engineer Principal

hydronics WHAT S WRONG WITH THIS SCHEMATIC?

Installation, commissioning and servicing instructions

Modular Panel System for Radiant Floor Heating MICRO-BOILERS MODULAR PANEL SYSTEMS

STAINLESS STEEL TRAP VALVE STATION

GLOBAL FLOW PRODUCTS

Applications and Piping Strategies for Condensing Boilers - Introduction

union swing check valve spring loaded check valve purging valve pressure relief valve relief valve metered balancing valve

InterSeptor Centrifugal Separators Operating & Maintenance Manual

"Best Practices in Modern Hydronic Heating - THE DETAILS

B. HI Compliance: Design, manufacture, and install pumps in accordance with HI "Hydraulic Institute Standards."

Wilo IL Vertical Split-Coupled Inline Pumps

Modular Panel System for Radiant Floor Heating.

Form 2143 Date: 4/3/03 Repl: 2/1/99 BRYAN STEAM LLC. Installation and Operating Service Manual BOILER FEED SYSTEM

CALEFFI. dirt separator series 01137/16 NA. Replaces 01137/15 NA. Product range. Technical specifications

Domestic Pump Condensate Transfer Equipment

SECTION STEAM AND STEAM CONDENSATE SPECIALTIES

Air Vents for Hot and Chilled Water Systems

! WARNING. Replacement Head Mechanism INSTRUCTION MANUAL MM-413F

Hydronic Mechanical Panels

Chiller Plant Design. Julian R. de Bullet President debullet Consulting

SECTION PUMPS. 6. Section Steam and Condensate Piping and Specialties.

A hydronic system controls comfort by delivering heated or cooled fluid to the conditioned space through pipes.

HVAC No. MFG Part No. Description Size Price

PRE-ASSEMBLED RADIANT CONTROL PANEL INSTALLATION MANUAL

MODEL P. 2 ft. NPSH Cast Iron Bronze Fitted Low NPSH Centrifugal Pumps. BULLETIN 112 Revised 7/09. PH (Horizontal Flange Mounted)

Blowdown Separator & Aftercoolers Installation, Operation, & Maintenance

Product Family Overview

DISTRIBUTION SYSTEMS. Water Piping and Pumps

Application Guide. Vitodens 100-W B1HA/B1KA Residential Boiler

Blowdown Separator & Aftercoolers

AM SERIES BOILER INSTALLATION FORM

INSTRUCTION MANUAL HS-208REVI

2019 PLUMBING AND HYDRONICS CATALOG

SAMPLE. added benefit of reduced operating costs during low demand periods, such as spring and fall.

Circulators high efficiency ECM Circulators

Installed together 5 year warranty

HORIZONTAL FIRE TUBE BOILERS Piping (HVAC) Pumping Equipment (HVAC).

! WARNING. McDonnell & Miller Installation & Maintenance Instructions MM-214(C) Series 61 Low Water Cut-Off OPERATION

Hard-hitting Contenders In HVAC Fluid Handling Solutions

Daikin Water Cooling, Heating, and High Capacity Booster Coils

Advanced Heating & Hot Water Systems

AIRPORT PLUMBING DESIGN STANDARDS REV. 2 11/02/2015

Steam and Condensate Pipe Sizing Health Care Example: Steam and Steam Heat Exchangers Basics (Part 7)

Chapter 2.3: Steam System

VSA SEWAGE PUMP. Capacities to 1600 gpm, Heads to 120, Horsepower range 3/4 thru 40, 3 thru 6 discharge, 1750 and 1150 operation.

Title: YALE OFFICE OF FACILITIES PROCEDURE MANUAL Chapter: 01 - Yale Design Standard Division: HVAC Standards

Akva Lux VX District heating substation for indirect heating and domestic hot water systems

Our Know-How. Your Peace of Mind. Steam Solutions

Liquid Drainers LIQUID DRAINERS

MODULEX BOILER INSTALLATION FORM

Series 1140 and 1141 Temperature Regulators

.2 Section Waste Management and Disposal..5 Section Performance Verification of Mechanical Piping Systems.

SENTRA Series Water Unit

Technical Data Manual Model Nos. and pricing: see Price List

HYDRONIC COMPONENTS & SYSTEMS

Bell & Gossett Circulators and Hydronic Specialties for Heating and Potable Water Systems Bell & Gossett

Powerful intelligence. Breakthrough functionality. SV2 Series Intelligent Safety Shut-off Valve

Industrial Processing Solutions

Removal of Non-condensable Gases and Air Is Critical In A Steam System

Best Practices for Condensing Boilers

Installation, Operation and Maintenance Instructions for Thermax Semi-Storage Calorifier

Geothermal Flow Centers. Simply Smart. boschheatingandcooling.com

SPIROVENT JUNIOR. Microbubble Separators Dirt Separators Combination Air/Dirt Separators. The Ultimate in Distribution Efficiency

J SERIES. Technical Specifications. Centrifugal Pumps for J Series Condensate & Boiler Feed Pumps. Features

HumidiPack,HumidiPackPlus and HumidiPackPlus CF Steam Humidifier Systems

Dirt and Air Separators

SECTION PLUMBING EQUIPMENT Piping (Plumbing). 2. Division 16 - Electrical Wiring and Connections.

Transcription:

Threaded Flanged Model PSH Primary Secondary Header A-451

The History of Primary-Secondary Pumping Did you know that Bell & Gossett invented Primary-Secondary Pumping? This widely popular pumping arrangement was conceived by B&G in 1954. It was originally developed as a method of increasing allowable system temperature drops while protecting the boiler. In fact, this method allows low and medium temperature systems to be used while maintaining the temperature drops usually seen in high temperature systems. It also holds the benefits of decreased pumping horsepower and improving system control. System control characteristics were made smoother because the pressure drop across the control valves caused by a single high head pump has been eliminated. This method proved to be a success, and to make it simpler, the first primary-secondary device was born just a few years later the B&G Primary-Secondary Fitting. It provided a simplified and fool-proof method of installing primary-secondary circuits. FIGURE 1: B&G PRIMARY-SECONDARY FITTINGS More than fifty years later, the primary-secondary pumping arrangement is still widely used. It still provides the same advantages as always, but at a higher rate when used with today s evolving equipment. The growing popularity of condensing and other modern boilers has made the use of primarysecondary piping more important. Ironically, these new style high efficient boilers have a greater flow resistance than their predecessors. However, by hydraulically separating the flow in each circuit, the flow through the high flow resistance boiler does not restrict the flow in the secondary circuits. This allows each leg of the circuit to be run at their optimal flow rates and temperatures, raising the overall system efficiency. We ve done it again! To simplify the piping arrangement and adapt to the ever-changing hydronic market, Bell & Gossett is proud to introduce the Primary-Secondary Header (PSH). This device simplifies the primary-secondary circuit pumping and eliminates several components. This results in cost savings since this single unit is less expensive and faster to install than the all the extra components. Description The B&G Model PSH, also known in the industry as a low-loss header, is a combination air separator and manifold that creates independent primary and secondary circuits. It is equipped with a purge valve allowing the user to remove any debris collected at the bottom of the vessel and an air vent to release air trapped in the system. Insulation also comes standard, eliminating the formation of condensate on the PSH body. 2

How does it work? The B&G PSH efficiently separates the primary and secondary circuits by acting as a closely spaced tee, which is normally seen in a traditional primary-secondary piping. However, the PSH does more than just separating the circuits this highly engineered product also acts as an air and dirt separator. The vessel is designed to create a low velocity area allowing air to rise to the top and sediment to sink to the bottom. Air Vent Air rises to the top Insulation Sediment sinks to the bottom Drain Valve FIGURE 2: B&G PRIMARY-SECONDARY HEADER (PSH) There are three possible flow paths, which are all dependent on the flows within the primary and secondary circuits. Flow Path #1: Flow in the primary circuit is equal to flow in the secondary circuit (refer to Figure 3). This is an example of a balanced flow where the flow and temperature from the boiler is equal to that of the distribution system. The hot water from the boiler remains near the top two ports, Port 1 and Port 2. A similar situation occurs on the bottom ports, Port 3 and Port 4 the flow and temperature from the system are equal to the flow and temperature of the fluid going back to the boiler. In cases like this, mixing with the PSH body is very minimal. T 1 = T 2 Q 1 = Q 4 T 3 = T 4 Q 2 = Q 3 T1 T2 Q1 Q2 Port 1 Port 2 T4 Q4 T3 Q3 Port 4 Port 3 FIGURE 3 3

Flow Path #2: Flow in the secondary circuit is greater than flow in the primary circuit (refer to Figure 4). Since the flows are no longer balanced, the temperature going to the secondary circuit is no longer the same as the temperature from the boiler. This is primarily due to mixing of the supply and return fluids within the PSH body. To satisfy the system demand, a portion of the fluid returning from the system at Port 3 mixes with the fluid entering the PSH from the boiler at Port 1. This situation results in a lower temperature flow at T 2 going to the system. The formula to calculate T 2 is shown in the appendix on the back page. T 1 > T 2 Q 1 = Q 4 T 3 = T 4 Q 2 = Q 3 T1 T2 Q1 Q2 Port 1 Port 1 T4 Q4 T3 Q3 Port 4 Port 3 FIGURE 4 Flow Path #3: Flow in the primary circuit is greater than flow in the secondary circuit (refer to Figure 5). This is another case of an unbalanced flow. This time, the system requirement is less than the boiler output. The flow returning from the system, Q 3, mixes with the hot water from the boiler, Q 1. This results in an increase in boiler return temperature. The formula to calculate T 4 is shown in the appendix on the back page. T 1 = T 2 Q 1 = Q 4 T 3 < T 4 Q 2 = Q 3 T1 T2 Q1 Q2 Port 1 Port 2 T4 Q4 T3 Q3 Port 4 Port 3 FIGURE 5 4

In all three cases described, the air and dirt are separated from the fluid as it enters the PSH body. The air rises to the top vessel and vented to the atmosphere via the automatic air vent while the sediment sinks to the bottom, which could be removed through the drain valve. Equipment Selection The basis of selection begins with the determination of the flow rates in both primary and secondary circuits. The greater of the two flows is the deciding factor in selecting the equipment. The table below may be used to select the suitable PSH for the application. Please note that higher flow rated than recommended will affect the performance of the product. Model PSH-1 PSH-1 1 /4 PSH-1 1 /2 PSH-2 PSH-2 1 /2 PSH-3 PSH-4 Connection 1" 1 1 /4" 1 1 /2" 2" 2 1 /2" 3" 4" Max. Flow (GPM) 11 18 26 40 80 124 247 Piping Layout The PSH is multi-purpose equipment that replaces several components in the system, simplifying piping and reducing installation time. Zone 2 Air Separator and Air Vent Alternate location Zone 1 Zone 2 Alternate location Zone 1 Closely Spaced Tee Strainer Traditional Primary- Secondary Piping Primary-Secondary Piping Piping with with PSH PSH REPLACED BY PSH Benefits, Features and Functions: Hydraulically separates primary and secondary circuits. Separates and vents air from the system. Separates and collects impurities in the circuits. Provides ease of installation. No complicated piping. Reduces installation labor. Reduces amount of fittings and piping. Eliminates strainer, air vent, and air separator. Available in 1" and 4" connections. Epoxy resin painted steel body with brass air vents and drain valve. Insulation is standard. 5