Challenges of Fire Protection Upgrades in Existing Libraries. Campus Fire Safety Forum

Size: px
Start display at page:

Download "Challenges of Fire Protection Upgrades in Existing Libraries. Campus Fire Safety Forum"

Transcription

1 Challenges of Fire Protection Upgrades in Existing Libraries Campus Fire Safety Forum November 6, 2013

2 Presentation Overview Code Requirements Goals of Fire Protection Systems Life Safety Property Protection Questions and decisions to made when planning Design Basis for Protection Challenges During Design and Installation 2

3 Code Requirements Libraries are assembly occupancies New/Existing Assembly Occupancy: NFPA 101, Life Safety Code, 2012 edition Group A-3: International Building Code (IBC) 2012 edition 3

4 Code Requirements (cont) Fire Sprinklers IBC (Group A-3) Larger than 12,000 sq. ft. More than 300 persons Located above/below level of exit discharge NFPA 101 Location and type of construction (New/Existing) More than 300 persons (New) Fire Alarm IBC (Group A-3) More than 300 persons NFPA 101 More than 300 persons (New) 4

5 Unique Feature of Libraries Campus Centers and Gather Spaces Some of the oldest buildings on campus Ever changing layout in recent years as we move away from books 5

6 Unique Feature of Libraries (cont) Hours of operation Specific environmental requirements for both occupants and books Quite Specific temperatures and humidity Low levels of dust 6

7 Goals of Fire Protection Systems Life Safety to Building Occupants Property Protection for books Property Protection for collections and artifacts 7

8 Early Planning of FP System Upgrades Requires patient outlook on the process rarely can this be done correctly on short schedule Gather Stakeholders Library Staff, Facilities Management, FPE Develop goals for the proposed system upgrades Develop timetable for design and installation process Start educating key library staff about the proposed fire protection upgrades 8

9 Planning: Library Infrastructure Develop a list of questions that need to be answered to be able to start the design Do library stacks need to be modified to accept fire protection systems Inventory of materials and risks Library Goals are 75% Capacity to allow for new material Do the books need to shift Can t just move one book, need to move them all to keep order Can be very expensive 9

10 Planning: Fire Protection Systems What types of fire protection is desired Early warning smoke detection Fire Sprinkler protection Wet, Dry or preaction? Clean Agent Fire Suppression Systems 10

11 Planning: Fire Protection Systems Prepare Table to Summarize Pro s and Con s Impact on books and collections Installation Challenges Maintenance Challenges Required storage/mechanical spaces Cost Reliability False activation 11

12 Fire Protection Pro s vs. Con s Fire Protection System Advantages Disadvantages Wet-Pipe Sprinkler System Preaction Sprinkler System Water Mist System Inert Gas Clean Agent System Highly reliable. Easy to maintain and install. Reduces likelihood of false activation, as sprinkler piping is not filled water. Uses less water than traditional sprinkler system. Clean agent will cause minimal damage to contents. Uses water as extinguishing agent. Inadvertent discharge more likely than with a preaction system. Less reliable than traditional wetpipe sprinkler system due to added layer of detection. Requires additional maintenance compared with traditional wet-pipe sprinkler system. Added cost associated with this type of system. Additional costs and reduced reliability associated with doubleinterlock system vs. single interlock system. Higher likelihood for corrosion. Requires separate fire pumps and utility services within a one hour rated enclosure. Specific application must be linked to formal fire test. Floor space required for agent storage cylinders. Need for pressure relief venting. Difficulty maintaining agent concentration. 12

13 Planning: Access During Construction How is library used? How do you retrieve books in area of construction? Off Line for duration Allow Paging of Books via library staff Clean up each work day to allow public access How to decide? Library usage statistics Committee of Library Staff and Faculty Faculty proposed for future studies 13

14 Planning: Construction Logistics Construction Work Schedule Normal Hours Off-Hours (Premium Time) 14

15 Planning: Construction Logistics (cont) Work Plan and lay down areas? 15

16 Planning: Construction Logistics (cont) Noise Resonates through the building Limit noise to select hours each day Limit noise to select areas Limit noise and limit productivity 16

17 Planning: Construction Logistics (cont) Protection of materials Physical Protection Dust Protection Protection from Water 17

18 Planning: Construction Logistics (cont) Protection of materials Physical Protection Dust Protection Water Protection 18

19 Planning: Construction Logistics (cont) Protection of materials Physical Protection Dust Protection Water Protection 19

20 Questions 20

21 Case Study A 14 Story high rise Library Heavy use lowest 3 stories Limited use top 11 stories 21

22 Case Study A - Schedule 2 separate projects Phase 1 Lowest Levels FP System Infrastructure Phase 2 Upper Floors Use of building during construction Phase 1: Closed lowest levels Phase 2: Closed floors during construction 22

23 Case Study A Sprinkler Protection Wet pipe sprinkler system Zoned per floor Each aisle treated as separate room Interface of stacks and concrete construction 23

24 Case Study A Sprinkler Protection 24

25 Case Study A Material Access Construction on each floor for 10 working days Testing was completed prior to moving to next floor. Books were available to library staff once a day. Library at 90% of book capacity 25

26 Case Study A Construction Limitations All stacks wrapped in multiple layers of poly Inspected by library staff Noise allowed between 6am and 8:15am Hammer drills for hangers Core drills Moving pipe through building 26

27 Case Study A Construction Limitations Investigated quieter methods Power driven fasteners 27

28 Case Study B 7 Story 4 above grade 3 below grade 200,000 sq. ft. Heavily Used Facility 28

29 Case Study B - Schedule 7 year plan Year 1: Fire Doors Years 2-3: Fire Alarm, E-lights and Exit signs Years 4-7: Fire Sprinklers Always open and available Overnight work during summer Clean up each day 29

30 Case Study B Sprinkler Protection Wet pipe sprinkler system Multiple zones per floor Each aisle treated as separate room Keep pipe and sprinkler high as possible Sprinkler guards Avoid light fixtures 30

31 Case Study B Protection Scheme Fire Alarm Fire Sprinkler 31

32 Case Study B Protection Scheme Sprinkler Detail 32

33 Case Study B Material Access Construction Limited to portion of building each phase Testing completed at end of each phase Books were available to general public at all times Library at 100% of book capacity 33

34 Case Study B Construction Limitations All stacks wrapped in multiple layers of poly Inspected by library staff No issues with noise all work off hours Public Library Visual fire alarm notification each aisle per ADA More fire alarm wiring More fire alarm power supplies requiring more space 34

35 Case Study B Construction Limitations Many fire alarm strobes Changing stack heights Consider open (as shown) Consider filled with books Communication between Contractor and University 35

36 Case Study C Historic Building 5 Story 3 above grade 2 below grade 90,000 sq. ft. Light Private Use Public Special Collections Library Stacks Employee only 36

37 Case Study C - Schedule 2 Years Planning 10 month Construction Fire Code and Architectural Upgrades Building Offline Construction site 37

38 Case Study C Sprinkler Protection Wet pipe sprinkler system Multiple zones per floor Protect each aisle and level of tiered stacks Utilize fire pump 38

39 Case Study C Material Access Library staff and faculty determine books to remain available Move to offsite storage facility All others are encapsulated in plywood Limited access Library at 120% of book capacity 39

40 Case Study C Construction Limitations All stacks wrapped in poly and plywood Temperature and humidity continuously monitored No issues with noise all work off hours Security for protection of materials 40

41 Case Study C Special Collections Dispersed throughout inventory Library not willing to locate in dedicated area and protect with fire suppression system 41

42 Case Study C Special Collections Two major concerns of library Sprinklers close to materials: Will the sprinkler discharge physically damage the books? Building Fire Pump not on emergency power Will the sprinkler system work if normal power is lost 42

43 Case Study C Library Concerns Will the sprinkler discharge physically damage the books? Limited published information available Time frame did not permit testing What would testing yield for book failure Do we need to relocate books away from sprinklers Would impact extent of available storage 43

44 Case Study C Sprinkler Discharge Developed comparative study to assist staff in determining level of risk Box most fragile items psi Domestic Water Garden Hose, Shower Head, Faucet, Lawn Sprinkler, Kitchen Sink Spray Hose 118 psi Fire Sprinkler Worst Case Proposed Fire Sprinkler 1,000-2,500 psi Pressure Washer 44

45 Case Study C Fire Pump Risk based concern Emergency power is not required for fire pump Performed hydraulic calculations Incorporated minor piping changes into design Demonstrate that without fire pump sprinkler system would satisfy code 45

46 Summary Goals of Fire Protection Systems Decisions to made during planning Design Basis for Protection Challenges During Design and Installation 46

47 Thank you! Joe Watson, P.E. Hughes Associates, Inc 117 Metro Center Blvd, Ste 1002 Warwick, RI

COSTCO, SAN FRANCISCO A PRESCRIPTIVE AND PERFORMANCE BASED ANALYSIS OF FIRE PROTECTION SYSTEMS AND DESIGN

COSTCO, SAN FRANCISCO A PRESCRIPTIVE AND PERFORMANCE BASED ANALYSIS OF FIRE PROTECTION SYSTEMS AND DESIGN COSTCO, SAN FRANCISCO A PRESCRIPTIVE AND PERFORMANCE BASED ANALYSIS OF FIRE PROTECTION SYSTEMS AND DESIGN Presented by Ian Levine June, 2016 Photo courtesy of Google Maps PRESENTATION OVERVIEW BUILDING

More information

FIRE SAFETY INSPECTION REPORT

FIRE SAFETY INSPECTION REPORT FIRE SAFETY INSPECTION REPORT M.S.ATTIRES LTD. ACCORD ID: 10887 A. RAHMAN PLAZA, SHANSHONGAON, FATULLAH, NARAYANGONJ OTHER FACTORIES: AISA FASHION LTD.; PRINT GARDEN LTD.; S.M. COLLECTION LTD. February

More information

FIRE ALARM SYSTEMS & 780 CMR. Dave LeBlanc, PE, FSFPE March 17, 2015

FIRE ALARM SYSTEMS & 780 CMR. Dave LeBlanc, PE, FSFPE March 17, 2015 FIRE ALARM SYSTEMS & 780 CMR Dave LeBlanc, PE, FSFPE March 17, 2015 BIOGRAPHY David J. LeBlanc, PE, FSFPE BS EE & MS FPE - WPI 23 Years PE Technical Committee Member NFPA72 - National Fire Alarm Code NFPA3

More information

FIRE AND SAFETY PROJECT REVIEW REPORT

FIRE AND SAFETY PROJECT REVIEW REPORT 1. A001 2. A001 3. A001 4. D102/103 5. A102/103 *VA enforces/applies the National Fire Protection Association (NFPA) 101 (current edition is 2015) and not the International Building Code (IBC). Ideally

More information

SPRINKLER PROTECTION OF COMBUSTIBLE CONCEALLED SPACES WITH LESS THAN 6 BETWEEN OPPOSITE FACES IN CAVITY.

SPRINKLER PROTECTION OF COMBUSTIBLE CONCEALLED SPACES WITH LESS THAN 6 BETWEEN OPPOSITE FACES IN CAVITY. STATE OF LOUISIANA DEPARTMENT OF PUBLIC SAFETY AND CORRECTIONS OFFICE OF STATE FIRE MARSHAL CODE ENFORCEMENT AND BUILDING SAFETY 8181 INDEPENDENCE BOULEVARD, BATON ROUGE, LA 70806 800-256-5452 225-925-4920

More information

NFPA 45 NFPA 211 NFPA 1600

NFPA 45 NFPA 211 NFPA 1600 NFPA 45 NFPA 211 NFPA 1600 Prepared by: William E. Koffel, P.E., FSFPE Expertly Engineering Safety From Fire 1 Objectives Overview of the NFPA process Understand the scope and application of NFPA 45, NFPA

More information

FIRE SAFETY INSPECTION REPORT

FIRE SAFETY INSPECTION REPORT FIRE SAFETY INSPECTION REPORT RAISA FASHIONS LTD. ACCORD ID: 11741 PLOT# B63, BSCIC INDUSTRIAL ESTATE, KANCHPUR, SONORGAON, NARAYANGANJ OTHER FACTORIES: NONE February 27, 2015 Page 2 SUMMARY was surveyed

More information

Montgomery County Government Building and Codes Department 350 Pageant Lane, Suite 309 Clarksville, TN 37040

Montgomery County Government Building and Codes Department 350 Pageant Lane, Suite 309 Clarksville, TN 37040 Montgomery County Government Building and Codes Department 350 Pageant Lane, Suite 309 Clarksville, TN 37040 SPRINKLER SHOP DRAWINGS 2007 NFPA 13 and 2007 NFPA 24 Project: Listed items require sprinkler

More information

Florida Building Code Chapter 9 Fire Protection Systems Advanced Course

Florida Building Code Chapter 9 Fire Protection Systems Advanced Course Florida Building Code 2010 Chapter 9 Fire Protection Systems Advanced Course 1 Introduction This course will cover specific sections of Chapter 9 that relate to fire alarm systems. While many contractors

More information

FIRE SAFETY INSPECTION REPORT

FIRE SAFETY INSPECTION REPORT FIRE SAFETY INSPECTION REPORT PORTLAND TEXTILE LTD. ACCORD ID: 11873 PLOT NO. 14-15, SECTOR 6, CHITTAGONG EXPORT PROCESSING ZONE, CHITTAGONG OTHER FACTORIES: NONE November 3, 2015 Page 2 SUMMARY was surveyed

More information

Fire Prevention Coffee Break Training. May 2017

Fire Prevention Coffee Break Training. May 2017 Fire Prevention Coffee Break Training May 2017 Agenda Introduction Submittals - Phelan Changes to NFPA 13 - Phelan Questions and Answers Open Forum Please welcome our S ummer Intern Charlie Poppe Small

More information

Moving Target: A Case Study in Providing Fire Protection Below a Reconfigurable Concert Hall Seating System. Part 1: Concept Design

Moving Target: A Case Study in Providing Fire Protection Below a Reconfigurable Concert Hall Seating System. Part 1: Concept Design Moving Target: A Case Study in Providing Fire Protection Below a Reconfigurable Concert Hall Seating System Part 1: Concept Design 2 Amy L. Porter, P.E. (TX,VA, NM) AND Michael Wojcik, P.E. (AZ, CO, MA,

More information

UNIVERSITY OF ROCHESTER ENVIRONMENTAL HEALTH & SAFETY

UNIVERSITY OF ROCHESTER ENVIRONMENTAL HEALTH & SAFETY Revision No.: 11 Page 1 of 12 I. PURPOSE This procedure establishes a tool to help maintain a safe environment for all patients, visitors and staff by evaluating the loss of a life safety feature during

More information

FIRE SAFETY INSPECTION REPORT

FIRE SAFETY INSPECTION REPORT FIRE SAFETY INSPECTION REPORT A-PLUS IND LTD PLOT # 28, MILK VITA ROAD, SECTION #07, MIRPUR, DHAKA - 1216, BANGLADESH March 10, 2014 Page 2 SUMMARY was surveyed for fire safety on 3/10/2014 by Hughes Associates,

More information

Center for Life Safety Education

Center for Life Safety Education Center for Life Safety Education Fire Sprinklers 101 Introduction, Building Codes, and Water Supplies Reprinted with permission from NFPA 13, Installation of Sprinkler Systems, Copyright 2007, National

More information

FIRE SAFETY INSPECTION REPORT

FIRE SAFETY INSPECTION REPORT FIRE SAFETY INSPECTION REPORT HAN A HATS & CAPS LTD. ACCORD ID: 12339 DAG NO. CS &SA-115/117, RS-188/181, KHOTION NO. CS-128, SA-274, BAIPAIL, ASHULIA, SAVAR, DHAKA. OTHER FACTORIES: TEXTSTREAM FASHION

More information

FIRE SAFETY INSPECTION REPORT

FIRE SAFETY INSPECTION REPORT FIRE SAFETY INSPECTION REPORT N.A GARMENTS PLOT # 36, ROAD # 46, GULSHAN NORTH C/A, DHAKA OTHER FACTORIES: SIDKO LIMITED, SIDKO APPARELS LIMITED, DELTA TIES LIMITED April 17, 2014 Page 2 SUMMARY was surveyed

More information

FIRE SAFETY INSPECTION REPORT

FIRE SAFETY INSPECTION REPORT FIRE SAFETY INSPECTION REPORT AMITY DESIGNS LTD. HOUSE#7&9, ROAD#9 BLOCK D, SECTION #11MIRPUR DHAKA OTHER FACTORIES: NONE April 21, 2014 Page 2 SUMMARY was surveyed for fire safety on 4/21/2014 by Hughes

More information

Fire Prevention Coffee Break Training. February 2017

Fire Prevention Coffee Break Training. February 2017 Fire Prevention Coffee Break Training February 2017 Agenda FDC s - Lund Standpipes - Phelan Fire Alarm Testing Phelan/Dooley Questions and Answers Open Forum Standpipe requirement Standpipes are required

More information

Florida Building Code 2010

Florida Building Code 2010 Introduction Florida Building Code 2010 Chapter 9 Fire Protection Systems This course will cover specific sections of Chapter 9 that relate to fire alarm systems. While many contractors are familiar with

More information

Corrosion in Fire Sprinkler Systems Increasing Your Liability, Increasing Your Costs, and Shortening System Life

Corrosion in Fire Sprinkler Systems Increasing Your Liability, Increasing Your Costs, and Shortening System Life Corrosion in Fire Sprinkler Systems Increasing Your Liability, Increasing Your Costs, and Shortening System Life Jeff Merwin Director of Business Development Fire Sprinkler Monitoring / OEM Controls jeffm@pottersignal.com

More information

Module 3. Water-Based Suppression Systems (WBSS) Part II: Highlights of Code Requirements

Module 3. Water-Based Suppression Systems (WBSS) Part II: Highlights of Code Requirements Module 3 Water-Based Suppression Systems (WBSS) Part II: Highlights of Code Requirements 1 WATER-BASED SUPPRESSION SYSTEMS-PART TWO This module covers: 1. Ohio Building Code requirements and when and why

More information

Richard B. Alpert, P.E. Senior FPE, Clark Nexsen

Richard B. Alpert, P.E. Senior FPE, Clark Nexsen Richard B. Alpert, P.E. Senior FPE, Clark Nexsen Clark Nexsen is a Registered Provider with The American Institute of Architects Continuing Education Systems (AIA/CES). Credit(s) earned on completion of

More information

FIRE SAFETY INSPECTION REPORT

FIRE SAFETY INSPECTION REPORT FIRE SAFETY INSPECTION REPORT GLOBAL OUTWEAR LTD. PLOT # M/1, ROAD # 7, SECTION # 7, MIRPUR, DHAKA March 3, 2014 Accord - Bangladesh RMG Fire Safety Inspection Global Outwear Ltd. Page 2 SUMMARY Global

More information

Common Building Code Misinterpretations

Common Building Code Misinterpretations Common Building Code Misinterpretations Presented by: Ron Melucci, P.E. Technical Manager, FP Division Engineering Planning and Management, Inc. rbm@epm inc.com www.epm inc.com 508 875 2121 Engineering

More information

PLAN REVIEW SUBMITTAL GUIDE

PLAN REVIEW SUBMITTAL GUIDE PLAN REVIEW SUBMITTAL GUIDE Plans, specifications and other construction documentation for the initial plan review should be as complete as possible at the time of submittal. Use this convenient guide

More information

Recommended Amendments to the 2015 International Existing Building Code North Central Texas Council of Governments Region

Recommended Amendments to the 2015 International Existing Building Code North Central Texas Council of Governments Region Recommended Amendments to the 2015 International Existing Building Code North Central Texas Council of Governments Region The following sections, paragraphs, and sentences of the 2015 International Existing

More information

Renovation Program. Renovation Program GENERAL

Renovation Program. Renovation Program GENERAL Renovation Program GENERAL This program provides guidance and protocols for renovation projects in occupied, operational acute hospitals. Team building is essential to quality control and HFD Services

More information

NFPA Edition. NFPA 13 (2016 Edition) Hot Topics and NFPA 13 FAQ s. Highlights of 2016 Changes. Storage Commodity Classification 4/29/2014

NFPA Edition. NFPA 13 (2016 Edition) Hot Topics and NFPA 13 FAQ s. Highlights of 2016 Changes. Storage Commodity Classification 4/29/2014 NFPA 13 2016 Edition NFPA 13 (2016 Edition) Hot Topics and NFPA 13 FAQ s Committees created the First Draft at meetings between July 2013 and December 2013 Balloting ended in early 2014 First Draft decisions

More information

Laboratories and Hazardous Materials. Company Overview

Laboratories and Hazardous Materials. Company Overview Laboratories and Hazardous Materials Don E. Contois, P.E. Sam Sinapi Company Overview R.W. Sullivan Engineering (RWS) was established in 1945 and currently has 95 employees. RWS is a full service engineering

More information

By: Russell Bainbridge March 18th, 2016 FPE 596

By: Russell Bainbridge March 18th, 2016 FPE 596 By: Russell Bainbridge March 18th, 2016 FPE 596 Egress Analysis and Design California Polytechnic State University's Engineering IV building Fire Detection, Alarm and Communication Systems A warehouse

More information

9/23/ :47 AM. Second Revision No NFPA [ New Section after ] Submitter Information Verification. Committee Statement

9/23/ :47 AM. Second Revision No NFPA [ New Section after ] Submitter Information Verification. Committee Statement Second Revision No. 5501-NFPA 5000-2016 [ New Section after 29.2.1.2 ] 29.2.1.3 Bathtubs, bathtub-shower combinations, and nonemergency showers shall be provided with grab bars in accordance with the provisions

More information

CHAPTER 61G15-32 RESPONSIBILITY RULES OF PROFESSIONAL ENGINEERS CONCERNING THE DESIGN OF FIRE PROTECTION SYSTEMS

CHAPTER 61G15-32 RESPONSIBILITY RULES OF PROFESSIONAL ENGINEERS CONCERNING THE DESIGN OF FIRE PROTECTION SYSTEMS CHAPTER 61G15-32 RESPONSIBILITY RULES OF PROFESSIONAL ENGINEERS CONCERNING THE DESIGN OF FIRE PROTECTION SYSTEMS 61G15-32.001 61G15-32.002 61G15-32.003 61G15-32.004 61G15-32.005 61G15-32.006 61G15-32.007

More information

A. Hydraulic calculations shall be prepared in accordance with Chapter 23 of NFPA 13 with the following exceptions:

A. Hydraulic calculations shall be prepared in accordance with Chapter 23 of NFPA 13 with the following exceptions: SECTION 21 13 13 WET-PIPE FIRE SPRINKLER SYSTEM PART 1 - GENERAL 1.1 RELATED DOCUMENTS: A. The Conditions of the Contract and applicable requirements of Division 1, "General Requirements", and Section

More information

Will Clay Spring 2014

Will Clay Spring 2014 Will Clay Spring 2014 1. Project Overview 2. Prescriptive Requirements 3. Existing Requirements 4. Performance Evaluation 5. Conclusions RJA-Houston since 2010 Hired as FP/LS consultants by architect in

More information

Engineering and Design of Fire Alarm Systems

Engineering and Design of Fire Alarm Systems Engineering and Design of Fire Alarm Systems Presented by: John P. Stoppi Jr., PE, FPE, CBO, CFI Stoppi Engineering john@stoppieng.com About the Presenter: John P. Stoppi Jr., PE, FPE, CBO, CFI Dual Registered

More information

Revision May All designs must be submitted to FM Global for review and approval prior to issuing such for bids.

Revision May All designs must be submitted to FM Global for review and approval prior to issuing such for bids. SECTION 211300 FIRE SUPPRESSION SYSTEMS 1.0 All new and renovated buildings shall be provided with automatic sprinklers throughout and fire standpipe systems. The design and installation of these systems

More information

Panel. RFMA 2015 Feb 1 3, Cracking the Code. Importance of Safety. Rick Gerlach Moderator. Senior Director of Cintas

Panel. RFMA 2015 Feb 1 3, Cracking the Code. Importance of Safety. Rick Gerlach Moderator. Senior Director of Cintas Cracking the Code What a Facility Manager Needs to Know about Safety Codes in the Restaurant Industry Panel Rick Gerlach Moderator. Senior Director of Safety @ Cintas Mike Prestonise VP at ADA Compliance

More information

Welcome to the Keys to a Successful Fire / Life Safety Inspection and Sustained Tenant & Building Safety

Welcome to the Keys to a Successful Fire / Life Safety Inspection and Sustained Tenant & Building Safety Welcome to the Keys to a Successful Fire / Life Safety Inspection and Sustained Tenant & Building Safety 2017 Keys to a Successful Fire / Life Safety Inspection and Sustained Tenant & Building Safety First

More information

Emergency Planning for Institutional Facilities

Emergency Planning for Institutional Facilities Emergency Planning for Institutional Facilities Pacific ADA Emergency Preparedness Webinars Presented by: Kimberly Paarlberg, ICC Based on the 2015 edition of the International Building Code (IBC) and

More information

Emergency Evacuation Plan

Emergency Evacuation Plan Emergency Evacuation Plan A Guide to Help Episcopal Churches Reduce Risk to People and Property in the Event of a Fire 2000 Church Risk Management Services INDEX I. Emergency Action Planning General list

More information

Narrative Reports As Regulated by 780 CMR, Section 903.0

Narrative Reports As Regulated by 780 CMR, Section 903.0 EXHIBIT 20 Narrative Reports As Regulated by 780 CMR, Section 903.0 903.1.1 - FIRE PROTECTION CONSTRUCTION DOCUMENTS a. Basis (methodology) of design for the protection of the occupancy and hazard for

More information

Public. Mike Free Health. State of Alabama Department of

Public. Mike Free Health. State of Alabama Department of State of Alabama Department of Mike Free Building Construction Specialist Technical Services Unit Office of Facilities Management Public 334-206-5221 334-206-5177 Health Fax: 334-206-5890 Web Site: www.adph.org.facmgmt

More information

Life Safety Code NFPA 10 NFPA 13 NFPA 25 NFPA 72 NFPA 90A NFPA 110 NFPA 99 THE 2012 EDITION OF THE LIFE SAFETY CODE HOSPITAL EDITION SESSION #7

Life Safety Code NFPA 10 NFPA 13 NFPA 25 NFPA 72 NFPA 90A NFPA 110 NFPA 99 THE 2012 EDITION OF THE LIFE SAFETY CODE HOSPITAL EDITION SESSION #7 THE 2012 EDITION OF THE LIFE SAFETY CODE HOSPITAL EDITION SESSION #7 AGENDA: Life Safety Code Referenced Publications Overview Life Safety Code NFPA 10 NFPA 13 NFPA 25 NFPA 72 NFPA 90A NFPA 110 NFPA 99

More information

CONSTRUCTION REQUIREMENTS

CONSTRUCTION REQUIREMENTS CONSTRUCTION REQUIREMENTS Note: The buildings on the UCCS campus are divided into two categories: General Fund and Auxiliaries. General Fund Buildings include academic and administrative functions. Auxiliary

More information

Public Health Fax: Web Site:

Public Health Fax: Web Site: State of Alabama Department of Public Health Fax: 334-206-5890 Web Site: www.adph.org.facmgmt Mike Free Building Construction Specialist Technical Services Unit Office of Facilities Management 334-206-5221

More information

FIRE SAFETY INSPECTION REPORT

FIRE SAFETY INSPECTION REPORT FIRE SAFETY INSPECTION REPORT DANNY'S KNITWEAR LTD. ACCORD ID: 12228 SURABARI, GAZIPUR, SADAR, GAZIPUR Other Factories: ne October 17, 2015 Page 2 Fire Safety Inspection Report Introduction manufacturing

More information

An Overview of Extinguishing Systems for Computer Equipment

An Overview of Extinguishing Systems for Computer Equipment Risk Solutions An Overview of Extinguishing Systems for Computer Equipment Various types of automatic suppression systems are available for protecting computer equipment. This report discusses the uses

More information

Fire Protection Coffee Break Training May 2016

Fire Protection Coffee Break Training May 2016 Fire Protection Coffee Break Training May 2016 Introduction High-Rise Requirements Questions and Answers Agenda Overview Site Fire Access Aerial Access Power/Back-up Power Elevators and Access Sprinklers

More information

SURVEY ON FIRE SERVICE INSTALLATIONS FOR OFFICE BUILDINGS IN HONG KONG

SURVEY ON FIRE SERVICE INSTALLATIONS FOR OFFICE BUILDINGS IN HONG KONG SURVEY ON FIRE SERVICE INSTALLATIONS FOR OFFICE BUILDINGS IN HONG KONG E.C.L. Pang and W.K. Chow Research Centre for Fire Engineering, Area of Strength: Fire Safety Engineering The Hong Kong Polytechnic

More information

MECKLENBURG COUNTY FIRE MARSHAL S OFFICE

MECKLENBURG COUNTY FIRE MARSHAL S OFFICE Effective Date: 11/01/02 Purpose: MECKLENBURG COUNTY To establish a set of guidelines for performance testing of all newly installed or upgraded fire alarm systems in order to ensure that all devices and

More information

MINOOKA FIRE PROTECTION DISTRICT Fire Prevention Bureau Fire Inspector Rodney Bradberry Plan Review

MINOOKA FIRE PROTECTION DISTRICT Fire Prevention Bureau Fire Inspector Rodney Bradberry Plan Review MINOOKA FIRE PROTECTION DISTRICT Fire Prevention Bureau Fire Inspector Rodney Bradberry Plan Review Minooka Fire Protection District Maintaining Your Fire Safety Systems Fire continues to be a major threat

More information

PROPOSED CODE CHANGES FOR REVIEW BY THE FIRE CODE ACTION COMMITTEE

PROPOSED CODE CHANGES FOR REVIEW BY THE FIRE CODE ACTION COMMITTEE PROPOSED CODE CHANGES FOR REVIEW BY THE FIRE CODE ACTION COMMITTEE Developed by the Midwestern Regional Work Group CONTENTS Item 15 Limited area sprinkler systems Item 20 Scope of IFC Ch 7 Item 21 Fire-resistance-rated

More information

Applying Performance-based Fire Alarm System Design Part 4

Applying Performance-based Fire Alarm System Design Part 4 Fire Alarm Notebook by Dean K. Wilson. P.E. Page 1 Applying Performance-based Fire Alarm System Design Part 4 by Dean K. Wilson, P.E. Over the course of the last four issues I have continued to discuss

More information

Subject: Fire Protection Impairment Program Reference: NFPA (see bottom of page 5) Effective Date: August 2014 Distribution All YC Employees

Subject: Fire Protection Impairment Program Reference: NFPA (see bottom of page 5) Effective Date: August 2014 Distribution All YC Employees Subject: Fire Protection Impairment Program Reference: NFPA (see bottom of page 5) Effective Date: August 2014 Distribution All YC Employees Purpose: To establish procedures to be followed when a fire

More information

Releasing Systems. Rob Mennie Senior Consultant Gage-Babcock & Associates Ltd.

Releasing Systems. Rob Mennie Senior Consultant Gage-Babcock & Associates Ltd. Releasing Systems Rob Mennie Senior Consultant Gage-Babcock & Associates Ltd. Releasing Systems What is a releasing system? System designed to detect a fire Causes release of an extinguishing system in

More information

Fire Protection Coffee Break Training August 2016

Fire Protection Coffee Break Training August 2016 Fire Protection Coffee Break Training August 2016 Agenda Introduction - Phelan NFPA 13 versus NFPA 13R systems for Residential Occupancies - Homa NFPA 72 Record of Completion - Homa Questions and Answers

More information

FIRE SAFETY INSPECTION REPORT

FIRE SAFETY INSPECTION REPORT FIRE SAFETY INSPECTION REPORT TUBA GARMENTS LTD. PLOT # 1682, ANANDA NAGAR, MERUL BADDA, BADDA, DHAKA OTHER FACTORIES: NONE July 5, 2014 Page 2 SUMMARY was surveyed for fire safety on 7/5/2014 by Hughes

More information

CONTENTS. B. System Design and Performance Requirements

CONTENTS. B. System Design and Performance Requirements 15625 Water Chillers This document provides design standards only, and is not intended for use, in whole or in part, as a specification. Do not copy this information verbatim in specifications or in notes

More information

FIRE INSPECTORS GUIDELINES FOR PLAN REVIEWS AND INSPECTIONS OF NEW CONSTRUCTION / ADDITIONS AND CHANGE OF OCCUPANCY

FIRE INSPECTORS GUIDELINES FOR PLAN REVIEWS AND INSPECTIONS OF NEW CONSTRUCTION / ADDITIONS AND CHANGE OF OCCUPANCY FIRE INSPECTORS GUIDELINES FOR PLAN REVIEWS AND INSPECTIONS OF NEW CONSTRUCTION / ADDITIONS AND CHANGE OF OCCUPANCY PLAN REVIEWS SITE PLANS: 1) Access to buildings (Volume V NC Building Code sections 602.6.1

More information

MSC Guidelines for Watermist Fire Suppression Systems Procedure Number: E1-03 Revision Date: 02/16/2017

MSC Guidelines for Watermist Fire Suppression Systems Procedure Number: E1-03 Revision Date: 02/16/2017 Procedure Number: E1-03 Revision Date: 02/16/2017 References: S. T. Brady, CDR, Chief, Engineering Division a. National Fire Protection Association (NFPA) 750, 1996 Edition, Standard on Water Mist Fire

More information

OPWDD Fire Safety Level One Post Test

OPWDD Fire Safety Level One Post Test OPWDD Fire Safety Level One Post Test Date: Name: Title: DDSO / Agency: Work Location: Signature: 1. The most important single element of individual fire safety is a. A proper evacuation plan b. Staff

More information

Tire Storage. Michigan Fire Inspectors Society Fall Conference

Tire Storage. Michigan Fire Inspectors Society Fall Conference Tire Storage Michigan Fire Inspectors Society Fall Conference September 15, 2016 This material, including the illustrations, represent the opinion of the author and instructor. This material is not designed,

More information

High challenge warehouse case study Summary

High challenge warehouse case study Summary High challenge warehouse case study Summary February 19, 2010 Richard Gallagher Michael Gollner Zurich Services Corporation Objectives Review the results of the high challenge warehouse workshop Recognize

More information

Plan Submittal Checklist

Plan Submittal Checklist City of Aurora Public Works Department HIGH-PILED COMBUSTIBLE STORAGE Plan Submittal Checklist Building Division 15151 E. Alameda Parkway, Ste 2400 Aurora, CO 80012 303-739-7420 Fax: 303-739-7551 Project

More information

University of Houston Master Construction Specifications Insert Project Name SECTION DRY-PIPE FIRE SPRINKLER SYSTEM PART 1 - GENERAL

University of Houston Master Construction Specifications Insert Project Name SECTION DRY-PIPE FIRE SPRINKLER SYSTEM PART 1 - GENERAL SECTION 21 13 16 DRY-PIPE FIRE SPRINKLER SYSTEM PART 1 - GENERAL 1.1 RELATED DOCUMENTS: A. The Conditions of the Contract and applicable requirements of Division 1, "General Requirements", and Section

More information

One call protects it all.

One call protects it all. One call protects it all. 2 // Tyco Integrated Fire & Security Two industry leaders. One great resource. Driven by our shared passion for protecting the employees and operations of businesses and institutions

More information

FIRE SAFETY INSPECTION REPORT

FIRE SAFETY INSPECTION REPORT FIRE SAFETY INSPECTION REPORT MAHID APPAREL LTD ACCORD ID: 11956 NOWPARA, MADHABDI, NARSINGDI, DHAKA-1604 OTHER FACTORIES: NONE February 20, 2015 Page 2 SUMMARY was surveyed for fire safety on 2/20/2015

More information

FIRE SAFETY INSPECTION REPORT

FIRE SAFETY INSPECTION REPORT FIRE SAFETY INSPECTION REPORT YOUNG INTERNATIONAL PLOT NO. 32-36, SECTOR 5-CEPZ, CHITTAGONG OTHER FACTORIES: NONE July 20, 2014 Page 2 SUMMARY was surveyed for fire safety on 7/20/2014 by Hughes Associates,

More information

FIRE SAFETY INSPECTION REPORT

FIRE SAFETY INSPECTION REPORT FIRE SAFETY INSPECTION REPORT MAGPIE COMPOSITE TEXTILE LTD. 832/833, DEWAN IDRIS ROAD, AMTOLI, ASHULIA, SAVAR, DHAKA OTHER FACTORIES: NONE May 17, 2014 Page 2 SUMMARY was surveyed for fire safety on 5/17/2014

More information

PRINTED: 06/09/2017 FORM APPROVED CENTERS FOR MEDICARE & MEDICAID SERVICES OMB NO (X2) MULTIPLE CONSTRUCTION A. BUILDING 03 - A BUILDING

PRINTED: 06/09/2017 FORM APPROVED CENTERS FOR MEDICARE & MEDICAID SERVICES OMB NO (X2) MULTIPLE CONSTRUCTION A. BUILDING 03 - A BUILDING SUMMARY PROVER'S PLAN OF CORRECTION K 000 INITIAL COMMENTS K 000 A Life Safety Code Survey was conducted by the State Fire Marshal beginning on May 9th, 2017 and ending on May 10th, 2017. Adair Acute Care

More information

American Society of Safety Engineers Professional Development Conference June 9-12, Fire Protection. Stephen J.

American Society of Safety Engineers Professional Development Conference June 9-12, Fire Protection. Stephen J. American Society of Safety Engineers Professional Development Conference June 9-12, 2008 Session No. 101F Fire Protection Stephen J. Musur CSP, CFPS Chubb Group of Insurance Companies June 12, 2008 1 Fundamentals

More information

LIFE SAFETY & FIRE PREVENTION MANAGEMENT PLAN

LIFE SAFETY & FIRE PREVENTION MANAGEMENT PLAN Title/Description: Life Safety & Fire Prevention Management Department: Facilities Management Personnel: All Effective Date: 5/97 Revised: 7/00, 7/01, 7/02, 7/03, 7/04, 7/05, 7/08 LIFE SAFETY & FIRE PREVENTION

More information

Design & Construction Standards, Revised January

Design & Construction Standards, Revised January PART 1 GENERAL 1.01 Scope of Standard A. This standard provides general requirements of The University of Texas at Austin for the design and construction of standpipe systems to include combination standpipe

More information

2018 IFC Update. Based on the 2018 International Fire Code, (IFC ) Goal. Objectives. Content

2018 IFC Update. Based on the 2018 International Fire Code, (IFC ) Goal. Objectives. Content Based on the 2018 International Fire Code, (IFC ) The International Fire Code (IFC ), establishes minimum regulations for fire safety. This handout will identify important changes in the IFC from 2015

More information

ICC CODE CORNER 2015 International Fire Code

ICC CODE CORNER 2015 International Fire Code PART II GENERAL SAFETY PROVISIONS CHAPTER 4 EMERGENCY PLANNING AND PREPAREDNESS SECTION 401 GENERAL 401.1 Scope. Reporting of emergencies, coordination with emergency response forces, emergency plans and

More information

Fire Alarm System Fundamentals

Fire Alarm System Fundamentals Fire Alarm System Fundamentals Mircom is the largest and oldest privately owned fire alarm and life safety manufacturer in North America and 5th largest overall with 50 years of industry experience. Mircom

More information

Statue of Liberty: A Risk Analysis

Statue of Liberty: A Risk Analysis Statue of Liberty: A Risk Analysis Bruce Campbell, FSFPE VP DOE Services National Park Service Agenda Overview of Project Scope Evaluation Steps Task 1 Code Analysis Task 2 Fire Modeling Task 3 Egress

More information

FIRE SAFETY INSPECTION REPORT

FIRE SAFETY INSPECTION REPORT FIRE SAFETY INSPECTION REPORT KAROONI KNIT COMPOSITE RATANPUR, SHAFIPUR KALIAKOIR OTHER FACTORIES: NONE April 5, 2014 Page 2 SUMMARY was surveyed for fire safety on 4/5/2014 by Hughes Associates, Inc.

More information

MINOOKA FIRE PROTECTION DISTRICT Fire Prevention Bureau Fire Inspector Rodney Bradberry

MINOOKA FIRE PROTECTION DISTRICT Fire Prevention Bureau Fire Inspector Rodney Bradberry MINOOKA FIRE PROTECTION DISTRICT Fire Prevention Bureau Fire Inspector Rodney Bradberry Fire Alarm Systems Plan Review Checklist Date: Permit Number: Business Name: Address: Fire Alarm System Submittal

More information

STATE FIRE MARSHAL S REQUIRED FIRE PROTECTION SYSTEMS NARRATIVE REPORT

STATE FIRE MARSHAL S REQUIRED FIRE PROTECTION SYSTEMS NARRATIVE REPORT STATE FIRE MARSHAL S REQUIRED FIRE PROTECTION SYSTEMS NARRATIVE REPORT The interaction of fire protection systems can be extremely complex. The detection of a fire in a building by an automatic device

More information

Minimum Standards for Engineers Practicing Fire Protection Engineering in the State of Oklahoma September 14, 2016

Minimum Standards for Engineers Practicing Fire Protection Engineering in the State of Oklahoma September 14, 2016 1. Introduction The intent of this document is to establish minimum standards for the practice of fire protection engineering within the State of Oklahoma as conducted by licensed professional engineers.

More information

FIRE INSPECTION GUIDELINES FOR FOSTER GROUP HOME PARENTS Effective June 1, 2002, Update September 2011

FIRE INSPECTION GUIDELINES FOR FOSTER GROUP HOME PARENTS Effective June 1, 2002, Update September 2011 HCFMO Harris County Fire Marshal M.S. Montgomery Fire Marshal FIRE INSPECTION GUIDELINES FOR FOSTER GROUP HOME PARENTS Effective June 1, 2002, Update September 2011 EFFECTIVE JANUARY 1, 2007 These guidelines

More information

Fire protection for buildings

Fire protection for buildings Fire protection for buildings HI-FOG high-pressure water mist Ghelamco Group Protecting people, property and business continuity A fire in a building can lead to serious consequences. Even a harmless fire

More information

PACDA Application Forms. 5/15/2018 Aman Fire Protection Consultants 1

PACDA Application Forms. 5/15/2018 Aman Fire Protection Consultants 1 PACDA Application Forms 5/15/2018 Aman Fire Protection Consultants 1 PACDA Submission Forms Preliminary Approval Form Final Approval Form Hazards Material Approval Form 5/15/2018 Aman Fire Protection Consultants

More information

FIRE SAFETY INSPECTION REPORT REDPOINT JACKETS LTD, DHAKA, BANGLADESH

FIRE SAFETY INSPECTION REPORT REDPOINT JACKETS LTD, DHAKA, BANGLADESH FIRE SAFETY INSPECTION REPORT REDPOINT JACKETS LTD, DHAKA, BANGLADESH January 3, 2014 Redpoint Jackets Ltd. PAGE 1 SUMMARY The four story factory housing Redpoint Jackets Ltd. located in Dhaka Export Processing

More information

INITIAL FIRE ASSESSMENT REPORT (FAR)

INITIAL FIRE ASSESSMENT REPORT (FAR) INITIAL FIRE ASSESSMENT REPORT (FAR) Factory SQ Station, Plot # 221-223, Jamirdia, Valuka, Mymensingh Mymensingh 17 Jun 2014 The Alliance for Bangladesh Worker Safety Page 1/17 Factory 17 Jun 2014 Introduction

More information

Building Description Applicable Codes & Standards Prescriptive Requirements. Performance Based Design

Building Description Applicable Codes & Standards Prescriptive Requirements. Performance Based Design June 15, 2017 Building Description Applicable Codes & Standards Prescriptive Requirements Structural Fire Protection Fire Sprinkler Fire Alarm Means of Egress Performance Based Design 2 3 Semiconductor

More information

Are there any policies regarding outlets that contain USB ports?

Are there any policies regarding outlets that contain USB ports? Answers to the Questions Mark J. Blackburn, P.E., CFPS February, 2016 Question 1 Are there any policies regarding outlets that contain USB ports? There is no direct reference in code about these types

More information

International Fire Code 2006 Requirements for Construction Plan Reviews of Commercial and Multi-Family Structures

International Fire Code 2006 Requirements for Construction Plan Reviews of Commercial and Multi-Family Structures International Fire Code 2006 Requirements for Construction Plan Reviews of Commercial and Multi-Family Structures Please note this is not an all-inclusive list. The type and complexity of your project

More information

Annual Fire Safety Report

Annual Fire Safety Report 2014 Annual Fire Safety Report The Higher Education Opportunity Act (HEOA) requires that certain information pertaining to the Fire Safety in Student Housing Buildings of current or perspective students

More information

INITIAL FIRE SAFETY ASSESSMENT

INITIAL FIRE SAFETY ASSESSMENT INITIAL FIRE SAFETY ASSESSMENT Factory Plot No -246-249, Adamjee EPZ, Siddhirganj, Narayanganj Narayanganj 17 Jul 2016 The Alliance for Bangladesh Worker Safety Page 1/17 Factory 17 Jul 2016 Introduction

More information

INSPECTOR I SKILLS ADMINISTRATION

INSPECTOR I SKILLS ADMINISTRATION INSPECTOR I SKILLS ADMINISTRATION 1- Prepare inspection reports so that the report is clear and concise and reflects the findings of the inspection in accordance with the applicable codes and standards..

More information

Enclosure 4- RISK ASSESSMENT

Enclosure 4- RISK ASSESSMENT Enclosure 4- RISK ASSESSMENT RISK ASSESSMENT Risk is a potential that a chosen action or activity will lead to a loss of human or property. Risk assessment is a step for Risk Management. Risk assessment

More information

Code Red Consultants- Fire Door Inspection, Testing, and Maintenance 1/5/2018. Learning Objectives. NFPA 241 Implementation

Code Red Consultants- Fire Door Inspection, Testing, and Maintenance 1/5/2018. Learning Objectives. NFPA 241 Implementation NFPA 241 Implementation Presented by: Peter Harrod, P.E. Chad Farrell, P.E. Learning Objectives Scoping and Purpose At what project milestones is the property owner s involvement necessary? Who is responsible

More information

What You Need to Know about Residential Sprinkler Design

What You Need to Know about Residential Sprinkler Design What You Need to Know about Residential Sprinkler Design Melisa Rodriguez, P.E., NICET IV Design Services Supervisor, Fire Safety melisa.rodriguez@uponor.com www.uponor-usa.com The Residential Sprinkler

More information

Firefighting operations on multi-tiered vehicle stacking buildings F5-13 GD

Firefighting operations on multi-tiered vehicle stacking buildings F5-13 GD DESIGNER S GUIDE Firefighting operations on multi-tiered vehicle stacking buildings F5-13 GD Introduction When to use Scope Use this chapter to provide a consistent Fire and Emergency New Zealand position

More information

Service Requirements SEMI- ANNUAL ANNUALLY OTHER REF. REQUIREMENT

Service Requirements SEMI- ANNUAL ANNUALLY OTHER REF. REQUIREMENT 58 Fire protection equipment requires care and maintenance at scheduled intervals to assure it will operate properly and safely when needed. Only personnel who are trained and qualified to maintain the

More information

University of Maryland FIRE EVACUATION PLAN Columbus Center POLICE FIRE MEDICAL EMERGENCY - 911

University of Maryland FIRE EVACUATION PLAN Columbus Center POLICE FIRE MEDICAL EMERGENCY - 911 University of Maryland FIRE EVACUATION PLAN Columbus Center POLICE - 911 FIRE - 911 MEDICAL EMERGENCY - 911 Anyone discovering excessive heat, smoke, or fire will immediately sound an alarm and report

More information

Emergency Response Plan

Emergency Response Plan Emergency Response Plan Developing an Emergency Response Plan As a practice owner, you likely already have some form of an emergency response plan developed for your practice. Our desire here is to guide

More information